I recently fixed a fault on a lighting circuit. The fault became apparent after some work I had carried out - I rewired part of the circuit for an ensuite refit, plus some additions to other circuits supplied by the same CU. I needed to provide RCD protection to the circuits that I had worked on, so changed the main switch in the CU for an RCD (I know RCBOs would have been better, but it's an old MK sentry board which only covers part of the installation, and parts are getting hard to come by), and also changed the mis-matched 10A MCB protecting the circuit for a 6A MCB.
The fault started a couple of days later, randomly tripping the MCB, but not the RCD. The clients had noticed that sometimes (but not always) it coincided with them switching lights on or off, but not one specific light. And it would come and go. A day or 2 no problem, then it would return, tripping the breaker every couple of hours. One day it got so that the breaker couldn't be reset, a good thing in a way as it makes fault finding easier.
Eventually I found the fault at a light switch - there was a break in one of the cores of the 4-way switching for the 1st floor landing light. The 2 sides of the broken conductor were just about touching, causing some mild arcing, but this had only slightly damaged the insulation . Repairing the broken core with a wago fixed the problem permanently.
I hadn't worked on this switch, so it must have been damaged for some time, and I suspect the 10A MCB may have been put there by a previous spark to stop the tripping without actually fixing the problem.
What I don't understand is why a fault like this caused the MCB to trip? The circuit, with all lights on, was pulling ~0.75A (measured before the fault got so bad that the MCB wouldn't reset). The break was in series with the load (LED lighting). So where was the extra current, enough to trip the MCB, coming from?
The fault started a couple of days later, randomly tripping the MCB, but not the RCD. The clients had noticed that sometimes (but not always) it coincided with them switching lights on or off, but not one specific light. And it would come and go. A day or 2 no problem, then it would return, tripping the breaker every couple of hours. One day it got so that the breaker couldn't be reset, a good thing in a way as it makes fault finding easier.
Eventually I found the fault at a light switch - there was a break in one of the cores of the 4-way switching for the 1st floor landing light. The 2 sides of the broken conductor were just about touching, causing some mild arcing, but this had only slightly damaged the insulation . Repairing the broken core with a wago fixed the problem permanently.
I hadn't worked on this switch, so it must have been damaged for some time, and I suspect the 10A MCB may have been put there by a previous spark to stop the tripping without actually fixing the problem.
What I don't understand is why a fault like this caused the MCB to trip? The circuit, with all lights on, was pulling ~0.75A (measured before the fault got so bad that the MCB wouldn't reset). The break was in series with the load (LED lighting). So where was the extra current, enough to trip the MCB, coming from?