- Joined
- Apr 15, 2011
- Messages
- 469
- Reaction score
- 152
If there are high earth currents , you should clamp to know exactly what you are dealing with, as a server cabinet in arms reach of a service pipe etc; could provide a path to earth via that person.I would say that the 300mA RCD would be good to keep there in case of fire and as to risk to persons the 30mA rule would apply if persons could come in contact with the equipment.Also the method of installation of the circuit of the industrial socket dictates whether need for RCD or specifically labelled/ under supervision etc. I would be also be concerned as to the earthing integrity of each workstation back to the server room.If all earthing is common, then you may need to segregate the circuits involved and this way you may find parallel paths contributing to your earth leakage at the server.