Hi there.
My friend is building a new house. He has decided to put service point in and out building next to new house. A duct has been run from out building to house. I will be using 16mm three core to supply house db. I've decided to use rcbo's for circuits in the house. But I am unsure if the cable at the out building side should be rcd after the cut off to supply the house? Any advice would be appreciated.
 
Two things:

1) Check your calculations for voltage drop for the lighting - you might need to upgrade that 16mm to a 25mm depending on length of run
2) It would probably pay you to bring the incomer into a metal-clad consumer unit anyway as that way you have something to make your armoured off to and also can run some ancillary sockets and lights in the outhouse more easily.

No, you don't need to provide upstream RCD protection to the cable, but personally I would install it onto a DP MCB rather than a single.
 
The half storey is built in the roof space with dormers!!!

sounds like some sort of hobbit hole..........


[ElectriciansForums.net] Service point in out building

what the hell are you building over there ? lol.

;-)
 

Reply to Service point in out building in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
435
  • Locked
  • Question
I'm not sure where this thread is going or what you are demonstrating is by an electrician or yourself. It doesn't really matter as the forum...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top