i=p/u
we just nearly finished kitchen rewire for guy and he asking all sorts of other we jobs, done.
my question is this we only rewired kitchen and fitted new board with 30mA rcds. he is now asking about shaver sockets in two bathrooms... would these need to be rcd protected or could i just come off the lights..??
as these are selv
was only kitchen lighting we done but yes thers plenty of spare was n both sides of dual board.... so would you run two new cables from 1 mcb to two bathrooms.. hes on about a complete board change soon, but just not today...
as these are selv
Standard shaver sockets are not SELV (the clue is Separated ELV), they are actually electrical separated LV, similar, but the regulations governing their uses are different due to the differing voltage bands in which each operates.
When installing the shaver sockets, additional protection via an RCD will be required for ALL circuits in a location containing a bath or shower 701.411.3.3
Gets a few that one. Thats why it still says 230V on the outlet :o
You could fit an RCD spur in the loft (assuming upstairs bathroom) for the sake of getting it done and leaving?
The requirements of the Regulations, are (pre-ammendment) that: "Additional protection shall be provided for all circuits of the location, by use of one or more RCDs having the charcteristics specified in Regulation 415.1.1."
The ammendment has changed the wording to "all low voltage circuits".
To my mind the use of an RCD spur which would only protect part of a circuit, would not be acceptable.
well he only has 4 recessed spots in each bathroom, they all power showers now with pump being installed in garage attic... so so maybe looks like il have to rewire these lights aswell or do as someone says and use rcd fcu for lights and shaver socket.
but what im thinking is just use 6A mcb on rcd side and run two bathroom circuits off this. then pull all other cables back. and then thats his bathrooms upto date and kitchen. hes keen to get dome to standards not like when it was wired.. and the quick additions over the years..
yeah im nearly certain all lights are one circuit.. so would be running new feed from cu to switch...
so would you agree by protecting installing shaver socket ,id have to rcd the lights???
The best and most compliant method is to protect all the circuits in the bathroom with an RCD when you are making changes.
If you have just the one lighting circuit that is currently on a non RCD protected way in the CU and can move this cable from non RCD protected to an RCD protected MCB, then this is very easy (even if you need to extend the cable a bit). simple and straight forward compliance. There should be no need to run another cable from the CU to the switch, Just move the existing cable over in the CU.
Yeah, I know what you mean, can be a right mess some units.
Just take out the lighting line conductor and give it a tug and see which neutrals and cpcs move!! Just hope more cables don't pop out!
Disconnect those and see if there is any give on the cable then just tuck it all back at the point you need.
Ahh, just realised you have one 3036 board and your new board for the kitchen, so you will need to extend the cable. Just disconnect it and get it accessible, crimp on a new length of cable, and feed this back out of the old box and over to the new CU, not ideal but if the old cable entry is not accessible this can be done.
If it is easy to feed a new cable to a point where you can reach the old wiring coming down then you could crimp / heat shrink on there and pull out the old section.
ok cheers. just love to get into the fram of mind to tackle it, all good. lets say i was to replace the cu with dual rcd board for rest of house... what would be key things to look out for.. i dont think would be borrowed neutrals as is bungalow, but you never know.. this is an option..
Yes you need to RCD the lights as well, as soon as you modify the existing bathroom installation it must comply with the current BS7671:2008 ... in #8 I emphasised 701.411.3.3 says "ALL CIRCUITS OF THE LOCATION"
Moving light circuit shaver outlet will be tapped from to RCD side is a much better idea than mine.
I disagree though spin that it is "unacceptable". Not perfect, better than before, safe, well yes, but unacceptable, well, thats down to the designer and installer and signer of document!
Would it be safe though?
Yes one could argue that it would be safer than not having no RCD protection at all.
However it would not offer the same degree of safety as would be achieved by compliance with the Regulations.
As such it could not even be listed as a departure.
i=p/u, it will still require 30mA RCD protection.