Shed / caravan | on ElectriciansForums
Discuss Shed / caravan in the UK Electrical Forum area at ElectriciansForums.net
growler
Basingstoke
I need to supply a shed 30m from the house at the bottom of garden that will then supply 2 x caravan hook ups and potentially other sheds in the future. Do you think a 6mm swa would be appropriate ? Dint want to over do it but I want it to be adequate for future loads.
before we can even guess, you need to come up with an estimated load. you should be able to do your own calculations from that.
Required Cable Size
SWA 6mm 3C - 30M
Voltage Drop
6.26 Volts.
Percentage Drop
2.7%
Current Load
32.6 Amps
Max Cable Load[SUP]*[/SUP]
33.8 Amps
You would have 32A capacity with 6mm. After the caravans it does not leave much at all left over.
Your having a giraffe aint you mate?
Maybe I should of just asked about caravans as I don't have a scooby about them. The vans will be used for camping out so I guess they will be charging a mobile phone with the light on ? Not really pulling massive loads hey ?
Wind up, correct?????
Reply to Shed / caravan in the UK Electrical Forum area at ElectriciansForums.net
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Yes, that was actually something making me uncomfortable too, the bonding of it all. I need to have another look at it, I'm not sure if the...