Hi guys and girls,

I'm newly qualified and want to confirm my method is sound before I commence any work. I'm registered with my CPS so can notify new circuits in domestic.

I have a new customer that has asked for lighting and power to the garden shed (wood construction). The existing installation is an economy 7 setup, with 2 consumer units. The 24hr CU is a MK Sentry (Plastic) Dual RCD split board with no free ways. Supply is TN-C-S PME, no supplier isolator fitted. Bonding in place. E7 night rate CU is earthed via 24hr CU, 24hr CU to cutout.

The shed is approximately 12m from the house. The ground between the house and the shed is concrete, with no damage to be made to it.

The plan in brief:

  • Isolate DNO supply by pulling fuse - (my DNO permits this with scheme membership).
  • Replace existing henley block for 5 way DP to enable additional feed
  • Install MET & connect to cutout. From MET to both existing CU's and confirm readings.
  • Install Fused Switch (Lewden FS) via Henley
  • Fused Switch to 6mm T&E, through wall to Wiska adaptable box.
  • Wiska adaptable box to 6mm 3 Core SWA.
  • SWA will run via a catenary wire to shed, then clipped direct and brought into shed. At this point, I'll either use another adaptable box and move back to 6mm T&E or bring the SWA into shed and into lewden consumer unit.
  • Shed CU (63A RCCB, 16A MCB, 6A MCB) will provide lighting radial and power radial, installed within flexicon and metal sockets.

The shed/workshop is used quite a bit, but with no extreme power requirements. Sewing machine, lighting, electric heater.

I've attached a few photos and a sketch to give an idea - apologies, I'm no artist!

D.
 

Attachments

  • [ElectriciansForums.net] Shed consumer unit
    CU.jpg
    90.7 KB · Views: 30
  • [ElectriciansForums.net] Shed consumer unit
    CUTOUT.jpg
    92 KB · Views: 32
  • [ElectriciansForums.net] Shed consumer unit
    snip.PNG
    85.6 KB · Views: 29

Reply to Shed consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
460

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top