optician

Electrics to shed. No water or gas.
Consumer unit in the middle of the house at the bottom of a nicely decorated wall with concrete floors.
In other words, no chance of separate circuit.
All earthing present and correct.

Rcd covering kitchen circuit and others.


Thinking of connecting to said 4mm kitchen radial on a 32 amp breaker Zs .32 at this point(Double socket)
Run another 4m in 4mm t&e(under units) to outside wall.
Connect to 6mm 3 core swa for 30 m (down and under garden) to brick shed to supply a 20 amp radial and 6 amp lighting circuit. metal consumer unit.
Any thoughts greatly appreciated.

Dave G
 
Can you not exit through the rear of the CU or just below or above and form a new circuit? or is the CU full to capacity? it's just a thought, you could then exit the CU in PVC/PVC and joint to the SWA in an adaptable box, not being able to see the set up. it's only a suggestion.
 
In an ideal world it would be a new circuit but sometimes you've got to just work with what you've got. You would want some kind of double pole isolation in the house as in the event of a fault you would want to be able to isolate the outside part of the circuit so as not to affect the kitchen/other circuits on the same RCD. What's the design current of the brick shed? For example is it one light, one double socket or multiple sockets that are going to run heaters, tools, etc. How long is the existing 4mm² kitchen radial to base volt drop calculations on?
 
Yes 6 mm as i wanted to minimize volt drop, but also wanted a zs at shed that was low. As the point of connection to the kitchen
circuit there is already .32 impedance.
The kitchen circuit is protected with an Rcd which covers others so if in future there is a prob with the circuit tripping others i
can put it in its own CU. Its the cable i have no chance of running.
Only computers in shed with lighting no heavy heaters etc
 
Yes 6 mm as i wanted to minimize volt drop, but also wanted a zs at shed that was low. As the point of connection to the kitchen
circuit there is already .32 impedance.
The kitchen circuit is protected with an Rcd which covers others so if in future there is a prob with the circuit tripping others i
can put it in its own CU. Its the cable i have no chance of running.
Only computers in shed with lighting no heavy heaters etc


With a Zs at the point of connection of .32 using 4mm² 3core swa on a 32A type B mcb using the 3rd core as a CPC would roughly give you a maximum length of around 69 meters from the point of connection. Probably wouldn't comply for volt drop though.
 

Reply to Shed Electrics in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top