I want to put a 2 way consumer unit into my shed to feed 2 outdoor sockets and a couple of spot lights.

I have bought the CU with a 63 A main switch, 1 x 20 amp for sockets and 1 x 6 amp for lighting,
now my question is, can I take a supply from my kitchen socket (fed from a 16 amp mcb) through the wall to the shed in 2.5 mm or 4.mm cable into the 63 amp main switch?

If that's not sufficient then what size cable to go from my house CU to shed CU (under 20 meters away) and can i connect that to a 35 amp mcb or do i have to connect it to a 63 amp?

I don't want to do a FCU as I may add more lighting in the future and a CU looks neater.

Thanks, Ryan.
 
Hi,

There's loads of threads on here regarding shed supplies. If you have a search, I'm sure you're find some useful stuff.

If it's an area you're unsure of, you'd be best to call in a qualified electrician who can install a supply neatly and safely.
 
I know its a pain like haha, but I've been through and cannot find anything that relates with having a 63 amp main switch, I have completed my electrical 2330 course and passed I'm just unsure of this situation, I am confident I can complete the work so I'm not gonna hire another "me" I'm just after a little in-put.

I can go from the house CU with no problem, I just wanna know if there's anyway I can go from a Kitchen socket (16 amp mcb) to the shed CU (63 amp) or another socket from upstairs on a (32 amp) to (63 amp) main switch.

Ryan.
 

I can go from the house CU with no problem, I just wanna know if there's anyway I can go from a Kitchen socket (16 amp mcb) to the shed CU (63 amp) or another socket from upstairs on a (32 amp) to (63 amp) main switch.

in a word. NO.. you can't feed a sub-main from an existing circuit. it mus come from the CU as a separate circuit.
 
I can go from the house CU with no problem, I just wanna know if there's anyway I can go from a Kitchen socket (16 amp mcb) to the shed CU (63 amp) or another socket from upstairs on a (32 amp) to (63 amp) main switch.

With all due respect, I do think you need a hand from somebody more experienced. None of us were born as skilled electricians - we all learned from somebody else and there's no shame in that.

I'm sure you're building your experience and in a couple of years you may well look back at this thread and understand why I'm suggesting you get a hand with this.
 

I can go from the house CU with no problem, I just wanna know if there's anyway I can go from a Kitchen socket (16 amp mcb) to the shed CU (63 amp) or another socket from upstairs on a (32 amp) to (63 amp) main switch.

in a word. NO.. you can't feed a sub-main from an existing circuit. it mus come from the CU as a separate circuit.

That's what I was after! .. looking I could have simplified the original question so sorry for that but thanks for all the replies!

ImpededLoop I'll take a note of that, Thanks!

Ryan.
 
I want to put a 2 way consumer unit into my shed to feed 2 outdoor sockets and a couple of spot lights.

I have bought the CU with a 63 A main switch, 1 x 20 amp for sockets and 1 x 6 amp for lighting,
now my question is, can I take a supply from my kitchen socket (fed from a 16 amp mcb) through the wall to the shed in 2.5 mm or 4.mm cable into the 63 amp main switch?

If that's not sufficient then what size cable to go from my house CU to shed CU (under 20 meters away) and can i connect that to a 35 amp mcb or do i have to connect it to a 63 amp?

I don't want to do a FCU as I may add more lighting in the future and a CU looks neater.

Thanks, Ryan.

I suggest that you ask the mods for access to the trainee section and ask the question there.

Announcements - Trainees Only
 
I've ran my 6mm cable, positioned, fixed and terminated all cables into the shed CU.

now for the connections to the house CU, the sheds main switch is 63 amps so what do you think is better to supply with? a 40 amp mcb or a 63 amp mcb on the RCD side from the house CU
 
I've ran my 6mm cable, positioned, fixed and terminated all cables into the shed CU.

now for the connections to the house CU, the sheds main switch is 63 amps so what do you think is better to supply with? a 40 amp mcb or a 63 amp mcb on the RCD side from the house CU

When you calculated the size of the cable you used what rating of OCPD did you use?
 
I've ran my 6mm cable, positioned, fixed and terminated all cables into the shed CU.

now for the connections to the house CU, the sheds main switch is 63 amps so what do you think is better to supply with? a 40 amp mcb or a 63 amp mcb on the RCD side from the house CU

This is the problem Ryan. You are carrying this out yet guessing it as you go along. You need to select MCB to protect your cable.
 
I want to put a 2 way consumer unit into my shed to feed 2 outdoor sockets and a couple of spot lights.

I have bought the CU with a 63 A main switch, 1 x 20 amp for sockets and 1 x 6 amp for lighting,
now my question is, can I take a supply from my kitchen socket (fed from a 16 amp mcb) through the wall to the shed in 2.5 mm or 4.mm cable into the 63 amp main switch?

If that's not sufficient then what size cable to go from my house CU to shed CU (under 20 meters away) and can i connect that to a 35 amp mcb or do i have to connect it to a 63 amp?

I don't want to do a FCU as I may add more lighting in the future and a CU looks neater.

Thanks, Ryan.
Thread of the month right here
 

Attachments

  • 10610865_10204553039251908_4622563899737294511_n.jpg
    25.2 KB · Views: 61
When you calculated the size of the cable you used what rating of OCPD did you use?
nk there's any sums been done here mate?
I don't.
Why do sums when you can guess and get baled out on here. This thread needs to be closed right now.
Ryan if you've got 2330 then I'm Santa Claus.
 

Reply to Shed/Garden Electrics? in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
457
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top