Aok1

I am bulding quite a large shed next and i need to get some power in. We currently have a re-wireable fuse board with 30mA rcd on the incoming supply.

I was going to run a 6mm swa from the board to the shed, terminate in a metal box then into a small CU with a few MCB'S.

Just need clarifacation on 2 things -

The supply is TNC-S but the shed will not have any conductive parts so i can export the earth?

No RCD needed in the shed CU? Discrimination problem if i did fit a RCD

Thanks
 
Despite whats been said on here before about outbuildings having to be on a TT there is absolutely no problem with using the TNCS earth for a shed. Only thing I would suggest is that you install a separate switchfuse at the intake for the SWA (not on the RCD) and install an RCD in the shed DB. That will get over the problem of a fault in your shed tripping the whole lot.
 
Small point of note, I detect from your reply you are apparently more comms then electrical, this project must comply with part P and be certified as such

Yes your right mate, but I do have a few years electrical experience. I also have 17th and a disq part p accreditation.
I will be notifying labc and using this for a elecsa assesment.
Thanks alan
 

Reply to the thread, titled "Shed power, is this right??" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top