Hi guys am new to this forum

Can someone give me advice on shed power

I am looking at running power supply to a shed which will have a small chest freezer and few sockets for dewalt battery charger I was going to run 2.5mm swa cable straight form house cu (which is rcd protected)
The shed is approximately 40m away
 
so at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?

30A would be 11.7V - .sensible if you have LED lighting.
 
so at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?

30A would be 11.7V - .sensible if you have LED lighting

so at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?

30A would be 11.7V - .sensible if you have LED lighting.
As stated its is for a a small chest freezer and the odd charger for drills ect
1 outdoor light and 1 batten style light I have answered the questions over and over

The 40A I measured up for was for over estimate in case later years I need anything else

I can not give any more information than what I already have

please only reply If its related not childish comments like above statement
 
Cannabis farm in a shed would be easy to find by local plod and a heat sensitive camera.
Same goes for normally cold roof space.

I think we were all a little surprised that you jumped 3 cable sizes after your first thoughts.

TBH, 2.5mm will probably be fine if it’s just a freezer, chargers and a couple of lights ONLY. Nothing else.
 
Cannabis farm in a shed would be easy to find by local plod and a heat sensitive camera.
Same goes for normally cold roof space.

I think we were all a little surprised that you jumped 3 cable sizes after your first thoughts.

TBH, 2.5mm will probably be fine if it’s just a freezer, chargers and a couple of lights ONLY. Nothing else.
It was just the long run i was worried about with the 2.5mm

As for the cable jump

the original idea was a radial circuit coming form my CU in the house plus I totally different radial for hot tub so two different circuits both in 2.5mm
( I haven't done cals for hot tub yet)

Or

The cable jump (10mm) was to power a brand new CU in shed its self then form that board ( shed ) I would power the hot tub heat and shed

Thank you kevin
 

Reply to Shed power in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now...
2
Replies
25
Views
2K
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top