Have just had a neighbour knock on my door and ask me to go round and look at a shed power supply he has attempted to install.
Layout is as follows:
House 32A MCB (63A RCD Protected) protecting downstairs ring - 13A Fused Switched Connection Unit (off downstairs ring) - 40A RCD 2 way Garage consumer unit
He has made all the connections from the fused connection unit off the downstairs ring, and connected those to the garage consumer unit into the RCD incomer
When he puts the RCD incomer switch on, the RCD on the house consumer unit trips.
I have checked Insulation resistance on cable between spur and garage is >299Mohm, between L-N, L-E and N-E.
No trip when the FCU is turned on and garage incomer is off, as soon as garage incomer is turned on, the RCD trips inside the house.
He has gone so far as to replace the RCD on the garage board with a main switch, and the problem is still there - he suspected the RCD's on both ends might be interacting with each other.
Please could someone kindly advise what I can look for as I am new to the job, having just completed my diplomas.
Thank you to all for their help in advance.
See below for image of the garage consumer unit he has fitted.
If the house rcd stays on with the spur on and the shed rcd off I would guess there is a fault on the shed circuits.
At a guess there is a light and socket circuit. So check these for faults.
Also the socket mcb needs swapping for a 16/20 amp mcb as its a radial circuit as the 32amp mcb is too big for the single 2.5 t&e
Edit
Saying that the supply is fused at 13amp by the spur unit off the house ring so the 32 amp mcb isn't too much of a problem
Hi All
Thank you for your responses so far!
So, I have removed ALL the circuits connected to the garage consumer unit apart from the incoming supply, and the RCD in the house still trips when the garage incomer is switched on.
From what I can see, the spur is wired correctly, as is the incoming supply into the garage consumer unit.
I can verify 230v incoming into the garage consumer unit between L-N.
When the garage supply is isolated (i.e. the 13A fused spur in the house is off), I have checked across L-N, L-E and N-E for continuity in the garage consumer unit - I get nothing across L-N, and L-E, but there is continuity across N-E.
Hi All
from that i'd suspect incorrect wiring at the FCU.
Reply to Shed Supply in the UK Electrical Forum area at ElectriciansForums.net
    • Friendly
Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...