C

craig1000

Thoughts please?

Shed supply spurred off ring in house, ring is RCD protected.
SWA glanded into AD box outside back entry through wall into socket!
At the moment SWA feed just a twin socket, but customer would like a small CU put in with a few sockets & couple of lights.
Although i would like to see it have its own supply from CU the cost & practicality's of it would be difficult.
I cant see anything wrong with the existing supply being used, its a 3c 4mm SWA.
Dont want to try to make the customer go for a dearer option unless i can justify it on safety/regs grounds that its not acceptable as it is.
 
ok so no extraneous parts i.e wooden shed, just normal use sockets n lights will be ok
If it was a metal shed or container then 10mm(or bigger if conductor size was larger) back to MET, if this was not practical then resort to earth rod!
 
Change outdoor adaptable box for IP rated fcu (or an indoor fcu in an IP encosure)

terminate swa into metal clad twin socket (or adaptable box then on to plastic sockets)

Couple metal clad socket to metal clad fcu for lights

simples.

(unless max demand in shed is more than 13amps, then it'll have to get more expensive)
 

Reply to Shed supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now...
2
Replies
25
Views
2K
  • Question
This same scenario popped up on the forum a little while ago. I’d be cautious of the point on the house rfc where you’re trying to get 2x 2.5...
Replies
2
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top