Stonesman

Chaps,

Got a call to check a solid plate hob in a local council youth club... staff have had 2 belts off it.

Above counter metal clad 45A switch is fed from a surface conduit direct from CU containing a 6mm T&E. Fed from a B32 from non-RCD side of wylex CU.

R2 checks out from hob to CU... 0.01 Ohm
Insulation L-E is >250 MOhm
Insulation N-E 30 MOhm
Zs at appliance is as near as damit Ze at CU

insulation test carried out with tails from hob disconnected from 45A switch. I'd expect the same result from L-E and N-E in a stand-alone appliance - is it just opposite ends of an element?

Want to make sure I've not missed anything before I give a clean bill... maybe I'm just being paranoid!

Stones.
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.

Reply to Shock off hob in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
419
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top