I like these sort of threads
Maybe my interpretation of BS EN 61439-3 is wrong......I see it that any device or factory wiring within the enclosure is covered for 16kA Breaking Capacity. I don't see that it would cover for thermal constraints of outgoing wiring from circuit breakers.
This is from Beama:
BS EN 61439-3 Annex ZB prescribes a specific conditional test arrangement relating to the use of
an upstream BS 88-3 (formerly BS 1361 type II) 100 A fuse-link. This 16 kA conditional test verifies
the performance of the incoming device, its connections, busbar, cable links, circuit-breakers,
residual current operated circuit-breaker and any other item in the consumer unit not separately
rated at 16 kA or higher. BS EN 61439-3 requires this rated conditional short-circuit current to be
identified by the symbol Icc and BS 7671 Regulation 536.4.201 references this symbol.