I like these sort of threads :)

Maybe my interpretation of BS EN 61439-3 is wrong......I see it that any device or factory wiring within the enclosure is covered for 16kA Breaking Capacity. I don't see that it would cover for thermal constraints of outgoing wiring from circuit breakers.

This is from Beama:

BS EN 61439-3 Annex ZB prescribes a specific conditional test arrangement relating to the use of
an upstream BS 88-3 (formerly BS 1361 type II) 100 A fuse-link. This 16 kA conditional test verifies
the performance of the incoming device, its connections, busbar, cable links, circuit-breakers,
residual current operated circuit-breaker and any other item in the consumer unit not separately
rated at 16 kA or higher. BS EN 61439-3 requires this rated conditional short-circuit current to be
identified by the symbol Icc and BS 7671 Regulation 536.4.201 references this symbol.
No that’s fair enough but I can’t imagine a case where the thermal constraints of a door bell transformer will be exceeded if protected by a class 3 limiting type B 6 amp 60898 device especially domestic installations if the csa is at least 1.0mm
 
No that’s fair enough but I can’t imagine a case where the thermal constraints of a door bell transformer will be exceeded if protected by a class 3 limiting type B 6 amp 60898 device especially domestic installations if the csa is at least 1.0mm

The I2t for 1.0mm is 13225 A2s. The Beama guide for 60898 Class 3 limiting states <35000 A2s for In <16A. I know in reality they are lower but manufacturers data would needed to confirm to confirm the energy let through of device. I have found some which are below this for their B6 devices.
 
It's a bit complicated isn't it? While we're on the subject of class 3 energy limiting devices...

Table B7 in the OSG gives minimum conductor sizes for class 3 mcbs, according to In and fault level. For a 6A with <= 3kA fault, minimum is 1.0mm. The beama guide you mentioned TJ gives I²t = 15000 for the same 6A/3kA, using adiabatic gives minimum 1.065mm². Do you think the difference is so small that it is ignored, margin of error?

(subtle difference - OSG gives fault levels whereas Beama guide give SC capacity, does it make a difference?)
 
I found manufacturer's I²t data for chint, wylex and hager MCBs, and put them though the adiabatic. As you said they give a considerably smaller conductor size compared with using model fault curve data, or beama data for class 3 devices. For all 3 brands, 1mm² was fine on a 16A breaker with the maximum 6kA fault
 
The penny is beginning to drop I believe. Please jump in and correct me if any of my assumptions are wrong:

The disconnection times don't apply to short circuits because they don't need to - the danger is from burning up the cables, not from electrocution. Energy let through and thin conductors are more of a concern.

Minimum conductor size can be calculated for a given fault using the adiabatic, and manufacturer's data is best as it will allow the smallest conductor size. For MCBs and RCBOs, the let through energy increases with fault current.

Sound about right?
 

Reply to Short circuit disconnection times in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top