Shower 8.5 on a 40mcb is it dangerous | Page 7 | on ElectriciansForums
Discuss Shower 8.5 on a 40mcb is it dangerous in the UK Electrical Forum area at ElectriciansForums.net
wales
Hi guys
My tenant just had an electrician in to connect her cooker and has told her that the shower is dangerous and not to use it because it has a 40 mcb in the consumer unit and it should be a 32.
The cable is 6mm and the shower is 8.5kw.
Can you advise me please
Thank you in anticipation
I do actually have a certificate of approval from NAPIT that states I am approved for electrical installation work in dwellings (A1.1) (Including Part P).
So it could be argued that I am 'Part P Approved' or 'Part P Certified'.
But again, I think most people understand that when someone says this, what that translates to is 'They are members of a competent persons scheme and are able to notify works in accordance with Approved Document P'... it's just easier to say Part P certified, of Part P approved or something akin to that.
Hi guys
I have exactly the same in my house, since upgrading my shower 7 years ago, with no problems, and will be fitting another to the same specification soon. One factor no-one has mentioned is circuit length. I believe a maximum of 10m (33') before a larger cable is required. If voltage at supply is greater than 230v (it usually is), longer could be used. I would verify voltage drop and RCD trip time to be sure.
Chris, this is the correct sized MCB for a 8.5kW shower, a 32amp device would be running at a slight overcurrent and although it would take a long time to trip it's not permitted in the regulations. I can't stand people who find fault with work unrelated to what they're doing - especially when they're spouting BS. :)
I confess that finding faults in electrical installations has been a favourite pass-time of mine for over 30 years! I agree entirely with the BS though: I've heard some lame excuses, and had my work criticised by many who should know better. It is a nuisance having to explain or pull out the Regs to show them. I try to always be open to constructive criticism, but no-one needs the BS, and I don't need the opinion of someone who born 20 years after I started working!
As an update I have now had a full inspection done took 4 hours and everything passed OK. thanks for all the replies.
Reply to Shower 8.5 on a 40mcb is it dangerous in the UK Electrical Forum area at ElectriciansForums.net
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...