- Joined
- Feb 20, 2011
- Messages
- 969
- Reaction score
- 425
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs and the cable type is shown as 2.5mm2 type A install methord C. I suspect a clerical error but as it is in the vendor document pack what would you suggest? The cooker is a four ring built in electric hob. The shower is an electricaly heated shower rateing of which to be checked tomorrow.
All the circuit insulation measurements are 500M ohm which is a bit sus.
All the circuit insulation measurements are 500M ohm which is a bit sus.
Last edited: