Hey all. Hope everyone is well.
Ok, I'm currently doing a rewire on a ground floor flat. The entire job will be done in trunking and I have an apprentice with me. Now, my intention is to run a 10mm cable to the shower as it's 9.5kw (I do this as a rule of thumb).
This is also in our company spec that regardless of situation, a new shower install is supplied via 10mm T + E. I am helping the apprentice do his colleague work and he is currently learning about maximum demand and diversity. He asked me how I come to the conclusion that it needs to be wired in 10mm. Well, got the brain ticking and I attempted to do a cable calc there and then but had a "brain fart"
I explained that we need to work out the design current (Ib). To establish this we divide power by volts and we get the maximum demand (please correct me if I'm wrong). So, this gives me aprrox 41A. Now, I believe we then need to select an appropiate protective device size ≥ of our obtained value.
This is where, well, I kind of fall flat on my face and I'd greatly appreciate some help. To give you an idea of the situation the length of run is approx 5m and it will be run throughout it's length in trunking but alone so as to save space.
I don't think any other factors apply. I basically would like the calculation of how to work it out and the answer and then I can not only explain to the apprentice how we worked it out but also give him some literature for study.
Don't worry guys I won't claim it I will say I asked the experts. Thanks :)
Ok, I'm currently doing a rewire on a ground floor flat. The entire job will be done in trunking and I have an apprentice with me. Now, my intention is to run a 10mm cable to the shower as it's 9.5kw (I do this as a rule of thumb).
This is also in our company spec that regardless of situation, a new shower install is supplied via 10mm T + E. I am helping the apprentice do his colleague work and he is currently learning about maximum demand and diversity. He asked me how I come to the conclusion that it needs to be wired in 10mm. Well, got the brain ticking and I attempted to do a cable calc there and then but had a "brain fart"
I explained that we need to work out the design current (Ib). To establish this we divide power by volts and we get the maximum demand (please correct me if I'm wrong). So, this gives me aprrox 41A. Now, I believe we then need to select an appropiate protective device size ≥ of our obtained value.
This is where, well, I kind of fall flat on my face and I'd greatly appreciate some help. To give you an idea of the situation the length of run is approx 5m and it will be run throughout it's length in trunking but alone so as to save space.
I don't think any other factors apply. I basically would like the calculation of how to work it out and the answer and then I can not only explain to the apprentice how we worked it out but also give him some literature for study.
Don't worry guys I won't claim it I will say I asked the experts. Thanks :)