Location
Manchester
Hey guys , went to a job last night to quote for a new shower install ... After removing the old shower front , I discovered 2 X 2.5mm t&e instead of 1 6mm .. the current shower is 8.5kw and ran into a 40a MCB on RCD side of a split board .. no signs of perished cables or burning anywhere ... Just wandering if ok to go ahead and replace or offer a new circuit in 10mm .. ? .. ps .. don't throw the book at me please haha ..
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
 
basically you have 2 x 2.5mm cables in parallel. if installed ref.method C, that gives you a Iz of approx 50A, so with a 8.5kW load (36A) Iz>In>Ib. unconventional, bit can't see a problem, asuming that the load is equally shared between the 2 cables. tin hat ready.

edit: what rating shower is being proposed?
Shower is 8.5kw .. Triton exite plus ..

Thanks ? I just wanted a second opinion as I've never seen it done like that before ..
 
You think they utilised an rfc to supply the shower? Why not run 6mm at the time.

id check there’s no sockets on the circuit as well.

is there an isolator before the shower?

very very strange.
 
If there is an option, I would likely run a new correctly sized cable. This install has questionable ccc due to installation method and cable lengths. And to me it smells like a short cut when it was originally installed. Just my personal view but other than our beloved RFC, any ccc that required 25mm or less should be realised in a single conductor (voltage drop considered separately:) ).
 
i had a full roll of 2.5mm on the van. nearest 6.0mm cable was 40 miles away, and the pub was opening in half an hour. no contest. ???. ( and i did give the customer the readings on a beermat).
 

Reply to Shower circuit help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top