I'd just like some views on my method for installing a shower circuit.

Plumber has asked me to install new shower circuit on a job he's doing, Customer has an old re-wireable CU, and doesnt want to pay for new CU change..

The only work i have been asked to do is install new shower circuit.. NOTHING ELSE.
So i wont be toucing the lights, Downflow heater or any other circuit in bathroom.

So i was going to split the tails at meter and install a dedicated shower unit, Just for shower, giving the shower 30ma protection, All other circuits will be on the old re-wireable board, as i will not have anything to do with these circuits..

I will be upgrading the bonding to incoming services, testing, and notification.

Job done..

Is there anything ive missed...??

And ok to leave other circuits on re-wireable board as wont be touching them..??
 
Yeah, I think most things boil down to "manufacturers instructions". You could say that the switching device would be protected by overcurrent such in the fact that it is unlikely that a fixed load is going to pull more current than it is designed for.

Just my thoughts...

Yes was thinking that myself but the reg clearly states 'shall be protected with a device' so I guess if no device is present for overcurrent then its not to regs.

I guess this is why a shower supply unit has RCBO.
 
Last edited by a moderator:

Reply to Shower circuit only RCD in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
786
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K
  • Question
ok cheers for the help lads
Replies
7
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top