D

Ducksy

Quick question guys shower needs downgrading was 10.5kw

Cable is 6mm on 40amp 60898 30mA RCD.

The 10.5kw element has failed so have advised customer a 8.5kw is more suitable for the cable/fuse size.

Do I need to issue a EICR for this as I'm changing the load.

I remember someone on here saying they only do MWC for replacing shower units on a related thread before (which I can't find), but you can't issue a MWC for a room containing a bath or shower.

What do you guys do.

Thanks.
 
but you can't issue a MWC for a room containing a bath or shower.

first i've heard of that. i would just complete a MWC. how is the 6mm run, ref. method? if anything other tan method C , i would downrate the MCB to 32A.
 
You see that's where the issue is, it's not like for like as I'm changing the load characteristic although be it lower.....what happens if I was changing it for a higher KW.

Your right of corse, just me over thinking it.

Thanks tele.
 
Work out the current carrying capacity of the cable after cable calcs applied and this is the rating of the shower you can fit .... if you protection device is a little higher than the cable ccc this is not a worry as the device wouldn't need to give overload protection as it is a fixed load and by the nature of it been a shower circuit it is unlikely to be added to, i.e if your cable after calcs was rated to 43amps and you fit a 9.5kw shower which draws 41.3 amps at 230v then fitting a 45amp or 50amp is acceptable although i stress you shouldn't be designing and installing circuits using this regulation if that was the case then a largewr cable would be necessary. I would only use this regulation if you are in your situe with a similar set up to the above calc.


Ps if the cab;e runs through a loft that hasn't een insulated yet then apply calcs as though it is insulated which you should do anyway or ensure cable can't ever be covered.
 
Last edited by a moderator:
you would ?
what happened to In >/= Ib ?
shame a 8.5kw shower pulls 37A lol.

as for cert , MWC will do as reducing the load doesnt require you to re-evaluate the circuit characteristics.
;-)
well it does Biff....but you know that an MCB to BSEN60898 will hold for 1.45 its operating current for upto an hour before letting go...it should be OK...unless theres 2 in that shower...undisturbed....lol..
 

Reply to Shower downgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top