The problem here is the short time the shower operates for,
Years ago our company added lots of heaters to a ring main in a school, despite me protesting as the QS that it was non compliant, and should be on a dedicated ring or radial circuits, every winter the circuit would trip after about 6 hours , I calculated there was a load of 4 x 12 Amps = 48 amps plus other stuff on the ring yet took 6 hours to trip on a 32amp ring !
 
The 32amp mcb will likely trip on overload as 9.5kw is 39amps at 240v or 41amps at 230v. Advise a down rate size of shower to suit cable or they need to upgrade it to 10mm2 for the 9.5kw
Is there any signs of over heating at all the terminals?

If the shower is rated 9.5KW at 240V then at 230V it's 38A.
 
Yes but a 32 amp mcb will take that for an hour plus
So what? It's still wrong isn't it....IMO it's simple, no code if the CCC based on design current is adequate taking installation method in to account. Code 2 if the CCC based on design current isn't adequate taking installation method in to account.
 
My own shower is a 9.5 kw on a 32 and 6.0mm , never trips no signs of damage , cable might be stressed but aren’t we all?
If the shower is rated 9.5KW at 240V then at 230V it's 38A.
I total agree with you leesparky
why post a question on here if you know the answer. not!
 
if installed ref. method C, 6.0mm is pessimistically rated @ 47A. what's the problem? shower is only 39.5A @ 240V, and that's probably over rated. bet a clamp meter would show no more than 35A. no code.move on.
 
if installed ref. method C, 6.0mm is pessimistically rated @ 47A. what's the problem? shower is only 39.5A @ 240V, and that's probably over rated. bet a clamp meter would show no more than 35A. no code.move on.
That only applies if clipped direct , none are always underfloor and through roof!
I still think 32 amp MCB is safe until shower circuit is rewired which was the point I was trying to make ?
 
Well that's another debate as some people may say cables installed underfloor boards should be reference method B
Others may not agree so the cable could be under the boards and chased and buried in the wall which may make it reference method C.
 

Reply to Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top