Got a call today to go to a old flat as the lady was getting shocks when she was having a shower.
She explained that when she touches the tap and then the shower unit she gets a tingle and now here daughter is getting them as well.
Considering the property is a rental I was amazed to see a old rewireable fuse with some retrofit Wylex MCB put in there.No RCD ,bit of old twisted uninsulated earth wire coming up from the supply cable buried in the wall.The fuse box was not a stand alone type unit it was integral in a metal type service cabinet about 2 foot tall.
The property has an earth 0.6 (TN-S) however it only goes to power circuits,the lights have no earth and the circuit feeding the shower pump.Pulling of a cover in the cabinet revealed about 3 cables out of 8 actually had a cpc in them.
Incoming water is bonded ,but not gas to this flat and next door.Wondering around my R2 Long lead could get no continuity on any taps ,shower.
There is no supplementary bonding anywhere,lots of plastic unions so continuity if it was there is now broken.
The shower has a pump and the boiler is a conventional type with a hot cylinder upstairs.No bonding in the airing cupboard.
Now I assume she is experiencing a difference in potential which is why she is getting shocks.I could not get any shocks with the shower running and checked for any voltage present just with my volt stick and direct measurement,non existed.
But why does she get it and the previous tenant did not ?
Apart from saying the flat should really be rewired and it is not really suitable for renting i need to provide a detailed explanation as to what is going on and why it has not happened previously.
If i upgraded and put in main bonding to services and run upstairs to bathroom from MET,also supplementary bonding in bathroom under bath and sink and airing cupboard would that fix it.
She has just signed for 6 months so not really practical to rewire now,if he actually wants to go ahead.
Any help greatly received
She explained that when she touches the tap and then the shower unit she gets a tingle and now here daughter is getting them as well.
Considering the property is a rental I was amazed to see a old rewireable fuse with some retrofit Wylex MCB put in there.No RCD ,bit of old twisted uninsulated earth wire coming up from the supply cable buried in the wall.The fuse box was not a stand alone type unit it was integral in a metal type service cabinet about 2 foot tall.
The property has an earth 0.6 (TN-S) however it only goes to power circuits,the lights have no earth and the circuit feeding the shower pump.Pulling of a cover in the cabinet revealed about 3 cables out of 8 actually had a cpc in them.
Incoming water is bonded ,but not gas to this flat and next door.Wondering around my R2 Long lead could get no continuity on any taps ,shower.
There is no supplementary bonding anywhere,lots of plastic unions so continuity if it was there is now broken.
The shower has a pump and the boiler is a conventional type with a hot cylinder upstairs.No bonding in the airing cupboard.
Now I assume she is experiencing a difference in potential which is why she is getting shocks.I could not get any shocks with the shower running and checked for any voltage present just with my volt stick and direct measurement,non existed.
But why does she get it and the previous tenant did not ?
Apart from saying the flat should really be rewired and it is not really suitable for renting i need to provide a detailed explanation as to what is going on and why it has not happened previously.
If i upgraded and put in main bonding to services and run upstairs to bathroom from MET,also supplementary bonding in bathroom under bath and sink and airing cupboard would that fix it.
She has just signed for 6 months so not really practical to rewire now,if he actually wants to go ahead.
Any help greatly received