Call out yesterday "my shower does not work".
Disconnected at the shower and C/U, no sign of a local pullcord or iso switch, home owner does not know if they have one?
Test results IR ranged from 2-15 M Ohms in between all conductors! No sign of recent building works or DIY, cable and shower installed about ten years ago so should not be giving these results.
Traced the 10mm t&e from the cu to a switch hidden under the kitchen cupboard. At last we find the problem.
This is what happens when terminations are not tight enough or the cables are squeezed together, touching with force in the back box. Notice the melting insulation on the conductors were they have been touching since install. Note to you all, use a double back box and keep the cables away from each other.
Disconnected at the shower and C/U, no sign of a local pullcord or iso switch, home owner does not know if they have one?
Test results IR ranged from 2-15 M Ohms in between all conductors! No sign of recent building works or DIY, cable and shower installed about ten years ago so should not be giving these results.
Traced the 10mm t&e from the cu to a switch hidden under the kitchen cupboard. At last we find the problem.
This is what happens when terminations are not tight enough or the cables are squeezed together, touching with force in the back box. Notice the melting insulation on the conductors were they have been touching since install. Note to you all, use a double back box and keep the cables away from each other.