I wire mobile decontamination units and we have a large unit that requires 4 electric showers.

Normally we use a standard metal 4way CU with rcd and mcb for each shower and its own 32A plugin inlet.

I would like to put all showers in the same board and have four 32A inlets coming from the board and each circuit separated inside.
It's possible all 4 inlets will be supplied by a onsite generator.
I can't seem to find any information on whether this is bad practice but also can not think of a reason why we can't do it.
The electrician who has just left the company said it was bad practice
 
If you are feeding the showers from 32A supplies, adding an MCB inside the trailer is unnecessary as the supplies should be protected by a 32A MCB at source. Although maybe it is a good idea to have one as an extra layer of protection when dealing with unknown supplies. An RCD would certainly be a good idea if you can't guarantee there is one on the other end of the supply.

It might be worth wiring the showers direct to the 32A inlets (via an isolator) and then looking at event style power distribution units to convert from the incoming supply if it is to be used in different locations with different sized supplies.
 
Thanks for the comments.

At the moment we are using a small 4 way db for each shower.
Problem is space the shower supply inlets are in quite a small cupboard located above the wheel arch.
The Customer request is 32A inlets and it is possible not all showers will be used at once but the option is available.
Our standard unit normally have 2 gas showers and 2 electric showers so space isn't an issue.
Suppose I will just go with the db for each shower route and struggle on.

Thanks for the help
 

Reply to Shower install problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes, that was actually something making me uncomfortable too, the bonding of it all. I need to have another look at it, I'm not sure if the...
Replies
2
Views
842
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top