It doesn't need to. It only needs to cope with the load. The 40A circuit breaker only needs to provide adequate fault protection.
I know, but you were not supposed to say that, hence my post to the young sparks, now where is the "I'm angry an experienced spark has trashed my post emoji?"
 
for 8.5kW, Ib= 36A, so unless the cable is covered in insulation, 6.0mm will be fine.
Agreed, no problem at all, the only question now to the OP is "why isn't it already up on the wall?"
 
Yes it does. Just not sure what the rating of the shower one is. A new board was put in about 5 years ago and I'm assuming all was ok for the 8kw shower we already have.
Assume! Not a good idea.

Did you get certification and building control notification when it was fitted?

If you did then I possibly would lean towards assumption everything is ok, but if it didn't I wouldn't.

Also it's had 5 years of deterioration.
 

Reply to Shower Installation 8kw to 8.5kw in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
531
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
272
The whole thing looks a bit of a mess, hanging cables and junction boxes, 15A fuse holder fitted to 30A base etc.
Replies
6
Views
296

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top