Shower interlock? | on ElectriciansForums

Discuss Shower interlock? in the Australia area at ElectriciansForums.net

Colin33

-
Arms
Joined
Jul 27, 2010
Messages
215
Reaction score
76
Location
Cornwall
About to do a consumer unit change and noticed that the 100a supply is feeding two electric showers. Clients say that the showers are not used simultaneously but may well be in the future. Does anyone know where to buy a 'non priority interlock' so that I can do this job properly and avoid any possible future problems? Mr. Google can't seem to find one :-(
 
agreed. anyway, the worst possible scenario is they'd have to have a cold shower and breakfast while waiting for DNO. not exactly life-threatening.
 
Two existing 10kw showers, will pull about 86A if used simultaneously. They haven't had problems in the past, but it's a big house which is being refurbished, including a garage to office conversion which will add extra load. While I'm at it, I wanted to make sure there's no future problems because if there is, no doubt it will be MY fault :) I've heard that the 'non priority interlocks' are expensive but I just wish to give the client the option....
 
Pulling 86A, the next biggest thing would be to have the cooker on with all bobs and grills a blazing. Worst case that's another 40a. All in all that is 126a + a little bit more. You'd have to run that all for a good hour or 2 before it trips out, I wouldn't worry mate ;)
 
I'm with the general comments that it shouldn't be a concern, but if you really want one Google 'ABB H-1122'

That finds links to ABB in Ireland, as well as a couple of previous threads on here on the same subject
 
Why not seperate them out onto a seperate board, with a suitable (say 63A) MCB feeding it from the main board? Worst case, they trip that MCB if both used simultaneously... though as others have said the 100A breaker *should* be up to the job, of course, that doesn't factor in anything else in the house like the cooker or fan heaters and so on...
 
Thanks for your comments guys... have now discovered that the electric oven is being replaced for a gas one, so feel a bit better about it now :) still interested to know where to get hold of a shower interlock should I need one at some point....
 

Reply to Shower interlock? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top