Hi Guys,

Searched the regs and internet and I cant find a definitive answer on whether they are needed to not. Found a few posts on here from a couple of years ago but there are a lot of mixed opinions.

I’ve got mixed views, always installed them but I don’t think they are very nessacary. Most of the time they break because the consumer uses them as a functional switch rather than a point of isolation.

Do we need them or can the MCB be used as isolation for maintenance and cleaning?

Thanks Dan
 
The problem is now that showers are becoming so ridiculously powerful that the domestic range of isolation become weak links due to their size and the inability to effectively connect the size of cable required to power them. Soon we will be seeing Glasgow isolators on the landing.
 
Most manufacturers insist on them...but I think they break because in general they are poorly made, and also quite poorly fitted.
The cannot insist on them. They can suggest them in their instructions. But manufacturers instructions are guidance only and don't have to be followed especially when they are wrong, (which is not unusual).
 
The cannot insist on them. They can suggest them in their instructions. But manufacturers instructions are guidance only and don't have to be followed especially when they are wrong, (which is not unusual).

So the regs state manufacturers instructions should be taken into account... how would you explain your decision not to fit a local isolator if the instructions explicitly state you should install one?
 
Even if it comes that a switch is not required, there will be absolutely, no chance what so ever of me clambering about in my roof space to pull the 10mm2 back and reconnect it directly into the shower, not ever.
 

Reply to Shower isolators - Do we need them or not? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
591

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top