Hi,

I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the CU cupboard to the loft. I know it's unconventional but is there any reason I can't use these cables to make a dedicated RFC for just the shower?

Thanks.
 
9Kw max on a 40A supply in my book.
customer needs a new cable or a new shower.
Alternatively, a "mate down the pub" to install what he has got instead of a professional electrician.

We all know it would work, but you cant document it or defend yourself it it all goes wrong.
Thinking about it...I tend to agree

My own house I would happily double up a couple 4 mm cables to make an 8mm cable if they were already there in situ and pop a 10kw shower on a B40 rcbo.

For a customer I would price to pull in a fresh 10mm cable or suggest get a lower rated shower
 
Using the 2*4mm if known to be new and broadly the same length is not really an issue for me, but it really ought to be on a 45A or 50A RCBO and they are not always so easy to get (especially in compact form like Wylex).

Which itself is odd, as I imagine a lot of 10+kW showers are in use...

I would be tempted to ferrule the ends together in to 10mm ferrules so they don't end up as 10.5kW on one 4mm run though.
 
Using the 2*4mm if known to be new and broadly the same length is not really an issue for me, but it really ought to be on a 45A or 50A RCBO and they are not always so easy to get (especially in compact form like Wylex).

Which itself is odd, as I imagine a lot of 10+kW showers are in use...

I would be tempted to ferrule the ends together in to 10mm ferrules so they don't end up as 10.5kW on one 4mm run though.
You can get ferrules for two cables, i.e. a 2 * 4mm^2 ferrule.
 
My own house I would happily double up a couple 4 mm cables to make an 8mm cable if they were already there in situ and pop a 10kw shower on a B40 rcbo.

But 2x 4mm cables doesn't make an 8mm cable. It makes 2x 4mm cables in parallel which has a much higher current rating than an 8mm cable.

4mm clipped direct could take 37A so 2x 4mm clipped direct could take 74A.
10mm clipped direct could take 64A
 

Reply to Shower on 4mm ring final circuit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
983
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
ok cheers for the help lads
Replies
7
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top