S

Sparky Stu

I am an adult trainee and i am trying to understand a problem that i must have with my shower pullcord isolater in my bathroom. Recently it has burnt out and was wondering what has caused this, as i have replaced this isolator a few times over the years.

The neutral cable on the load side is the cable that has always burnt out. The cable is 10mm and the length of run cannot be that great as c/u is located in the kitchen directly under my bathroom. The shower is 8.5kw on a 40A 60898 MCB.

Each time i have replaced this pullcord i have stripped the cable back to where the cable is in good condition. Just looking for some possible answers as cable is now beginning to get a bit on the short side from all the previous stripping back. Cheers Stu :)
 
Also make sure you use the units, power on/off switch to actually turn the shower off. Quite often people just use the pull cord to turn the shower off and therfore your switching under load, which will reduce the life of perhaps cheaper switches.

Thank you Malcolm, I don't really do domestic, but even I know that you MUST advise customers to NOT use the pull cord as an on/off switch. Hence the reason that I was taught to always shorten the cord, so that an adult would have to stretch to reach it.
 
Many thanks SimpleSimon.
Your spot on as per OSG but I am amazed that you could have a pull cord switch within zone 1 at all.I would never have it in my house with all that condensation in the shower,seems daft.
I must confess that all shower fitted I always locate a DP isolator outside,don't like pull switches seems old fashioned to me.
Thanks again.

I use pull cords but would never put in Zone 1 either for same reasons. Plus the string gets too wet n rotten.
 

Reply to Shower Pullcord in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
333
  • Question
Oh definitely, the amount of tails that I come across in consumer units barely nipped up is staggering, I always tighten them, wait a minute, give...
    • Like
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top