Work for a company who sub contracts to the local council and looking for some advice.
In the domestic properties the council have wired a shower pump off the load side of the showers in 2.5mm (40A RCBO) which then serves a 13A switched fused spur to feed the shower pump. I am unsure this is ok as a shower is a fixed load and worried about overload on the 2.5mm?
the council say it’s covered under section 434.2 but this relates to fault current. Can anyone provide some help on the matter,
Thanks
 
Work for a company who sub contracts to the local council and looking for some advice.
In the domestic properties the council have wired a shower pump off the load side of the showers in 2.5mm (40A RCBO) which then serves a 13A switched fused spur to feed the shower pump. I am unsure this is ok as a shower is a fixed load and worried about overload on the 2.5mm?
the council say it’s covered under section 434.2 but this relates to fault current. Can anyone provide some help on the matter,
Thanks

Providing there is a fcu to provide overload protection for the pump.

(A pump is NOT a fixed load)

And a fault on the 2.5mm (far end) cable before the fcu has a low enough Zs to provide ADS by the 40A MCB/RCBO ( or the use of the RCBO/RCD for fault protection instead of additional protection)

Then there isn't a problem.

I know many would feel uncomfortable, especially if the fcu is some distance away, but it is absolutely fine.

But it isn't a blanket OK - if there is no fuse or other overload protection for the smaller load (pump or ufh etc) then it would be unacceptable.

(some may say ufh is a fixed load so doesn't need overload protection - fair enough for the actual heating cable - but not so for the controller!)

The testing of the Zs at the smaller cable is critically important - a good Zs at the shower doesn't prove the whole of the circuit - so in your example if it was an MCB the Zs must be low enough for the 40A MCB at ALL points up to the fcu. (After the fcu the Zs has to meet the value for the 13A fuse).

Since you have a RCBO the Zs value merely determines if the RCD aspect is additional, or fault protection)
 
Providing there is a fcu to provide overload protection for the pump.

(A pump is NOT a fixed load)

And a fault on the 2.5mm (far end) cable before the fcu has a low enough Zs to provide ADS by the 40A MCB/RCBO ( or the use of the RCBO/RCD for fault protection instead of additional protection)

Then there isn't a problem.

I know many would feel uncomfortable, especially if the fcu is some distance away, but it is absolutely fine.

But it isn't a blanket OK - if there is no fuse or other overload protection for the smaller load (pump or ufh etc) then it would be unacceptable.

(some may say ufh is a fixed load so doesn't need overload protection - fair enough for the actual heating cable - but not so for the controller!)

The testing of the Zs at the smaller cable is critically important - a good Zs at the shower doesn't prove the whole of the circuit - so in your example if it was an MCB the Zs must be low enough for the 40A MCB at ALL points up to the fcu. (After the fcu the Zs has to meet the value for the 13A fuse).

Since you have a RCBO the Zs value merely determines if the RCD aspect is additional, or fault protection)
Thanks for the reply. Very helpful. My only concern from that was because showers run at a constant rate i.e 38amps, wouldn’t the 2.5mm where it is connected at switch end up having to deal with that current to some extent?
 
Thanks for the reply. Very helpful. My only concern from that was because showers run at a constant rate i.e 38amps, wouldn’t the 2.5mm where it is connected at switch end up having to deal with that current to some extent?
Depends how it is connected, which is of course a practical issue, the terminals are usually designed for 6/10mm cable so if you can ensure the larger cable makes direct contact with the termination, then the smaller cable isn't in the path.

If the smaller cable is squeezed between the main connections then yes, current would pass through this and could cause a hot spot

That comes down to plain good workwomanship - not really a direct aspect of the regs in general.

The bigger issue, is actually ensuring that the smaller cable makes proper contact, and isn't squeezed to the side ending up loose even though the termination is tight.

Again though, it's just good workwomanship 😀
 

Reply to Shower pump wired off shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
846
  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Excellent information, and thank you. Will suggest a local electrician could be asked to look into the possibility of tighter control for...
Replies
4
Views
7K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks