hi everyone
i have a question on a shower circuit the ccu is a crabtree sb6000 type,tn-c-s system,100a main switch split load 6 way 4 protected by 80a 30mA rcd with shower 40a,cooker 32a not used,32a sockets for all house,16a old immersion circuit now used to supply 3 pir 500w halogen floods off two seperate 5a sw/fused spurs, one is controlling 2 floods and the other controlling 1 flood and two lights in loft,on the other side is a 40a 30mA rcd protecting 2 6a light circuits the MCBs are all type 1 crabtree sb6000 except the shower which is a 40A type 2 crabtree 610 10mm cable 4mm cpc 45a pull switch shower 9.5kw at 240v 8.8kw for 230v
my question is about the adibiatic equation concerning cpc which i think is 280a x 280a x 5 sec square root divided by 115 for k value is this correct way of doing this calculationon a bs3871 type2 40A cb, which i get to 5.44 so it should be a 6mm cpc is this correct how ive come to this conclusion
the max zs for a bs3871 type 2 is 0.82ohms the max measured according to gn3 is 0.66 ohms
as this circuit is protected by a 30mA rcd then does this satisfy the regs i have not done any tests yet but i am going to do a ZE,continuity to check ZS,insulation resistance, pfc etc if i find that the measured ZS is larger than the MAX measured ZS should i try to get a type1 to replace the type 2 the type 1 has 160a 5 second type current charicteristic which when doing adibiatic would bring cpc size down to 3.11 so then the 4mm cpc would be acceptable and will also increase max zs to 1.44ohms and max measured value to 1.16 ohms
is this the best thing to do if it doesnt meet the adibiatic and ZS
does anyone know where i can get a crabtree 40a sb6000 type1 bs3871 cb from
any help and advice would be grateful cheers
 

Reply to shower question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top