Do you encounter many issues with homeowners experiencing "tingling" from electric showers in homes with a TT supply system?
Reason I ask is because everytime we respond to this issue it always turns out to be a result of a plumber replacing copper with Qualpex or the service provider replacing metallic with plastic. This results in the "TT" system having a much higher fault loop impedence and creates issues, regarding the functional earthing in the shower. Bearing in mind the much more common use of TT in the UK, is this a widespread problem for you?
Reason I ask is because everytime we respond to this issue it always turns out to be a result of a plumber replacing copper with Qualpex or the service provider replacing metallic with plastic. This results in the "TT" system having a much higher fault loop impedence and creates issues, regarding the functional earthing in the shower. Bearing in mind the much more common use of TT in the UK, is this a widespread problem for you?