I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt shower switches is that the stranded wires haven't been twisted and just put in straight.I always twist the standed cables to make one solid conductor before inserting into the terminal.My thoughts are that the screw only clamps a few strands when they are straight,leaving the other stands either side of the screw.With the load on a shower I feel this is a weak point and hence why they burn out.Obviously it can also be caused by loose terminals but back in the day when shower switches had two screws per terminal,I don't recall having to replace that many switches.Prehaps they should bring back the two screw method?
 
100% agree on the two screws, but equally as much disagree on the twisting. If a clamped, twisted cable is turned in the direction that untwists the strands, some of those strands can move up into the voids either side of the screw threads, leaving the remaining strands under the screw head insecure.
The correct method, IMHO, is to leave the strands straight and tighten the screw(s) while gently twisting and untwisting the cable, so that some of the strands completely fill the voids. This assumes a correctly designed fitting, where the diameter of the screw is a good proportion of the diameter of the tunnel for the cable, and that the diameter of the tunnel isn't massively greater than the cable.
 
With coarse stranded cables in screw terminals, I also tend to tighten, manipulate the cable and re-tighten. This process may be repeated two or three times until it's clear the cable is bedded nicely in the terminal and unlikely to loosen through thermal creep.
 
I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt shower switches is that the stranded wires haven't been twisted and just put in straight.I always twist the standed cables to make one solid conductor before inserting into the terminal.My thoughts are that the screw only clamps a few strands when they are straight,leaving the other stands either side of the screw.With the load on a shower I feel this is a weak point and hence why they burn out.Obviously it can also be caused by loose terminals but back in the day when shower switches had two screws per terminal,I don't recall having to replace that many switches.Prehaps they should bring back the two screw method?
I have also seen this many many times, IME it is due to loose connections and cheap switches.
 
I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt shower switches is that the stranded wires haven't been twisted and just put in straight.I always twist the standed cables to make one solid conductor before inserting into the terminal.My thoughts are that the screw only clamps a few strands when they are straight,leaving the other stands either side of the screw.With the load on a shower I feel this is a weak point and hence why they burn out.Obviously it can also be caused by loose terminals but back in the day when shower switches had two screws per terminal,I don't recall having to replace that many switches.Prehaps they should bring back the two screw method?

Replace with one of these.

 
Replace with one of these.



Better to use one of these

 
Whilst agreeing with comments above, I’ve always thought that the single largest challenge in installing these (of any type, though 100% recommend the new Click/Crabtree style) is simply that they’re a pain in the neck to fit because you’re working overhead, usually close to a wall on one side, with a tiny amount of slack on a big stiff cable. And, what gets me is that there’s not even an actual need for them in the first place!!
 
Whilst agreeing with comments above, I’ve always thought that the single largest challenge in installing these (of any type, though 100% recommend the new Click/Crabtree style) is simply that they’re a pain in the neck to fit because you’re working overhead, usually close to a wall on one side, with a tiny amount of slack on a big stiff cable. And, what gets me is that there’s not even an actual need for them in the first place!!

While I like the round switches, their weakness (Crabtree at least as I've not used Click) is terminal placement means fixing one cable before the base if located anywhere close to a corner.
 
Those round Crabtree ones are so near yet so far from being the perfect shower pull cord. The way the wire
While I like the round switches, their weakness (Crabtree at least as I've not used Click) is terminal placement means fixing one cable before the base if located anywhere close to a corner.
Yes, they've angled the terminal screws so if you put it in a corner then three screws are facing a wall, you have to wire it all up before you fix it to the ceiling.
 
Whilst agreeing with comments above, I’ve always thought that the single largest challenge in installing these (of any type, though 100% recommend the new Click/Crabtree style) is simply that they’re a pain in the neck to fit because you’re working overhead, usually close to a wall on one side, with a tiny amount of slack on a big stiff cable. And, what gets me is that there’s not even an actual need for them in the first place!!
yep I get your point, I hate them, my shower at the moment is off the combi boiler, but when I did have electric I had a 45 amp double pole switch on a deep twin patterice in an airing cupboard, so much room in it compaired to the pull switches fitted today
 

Reply to Shower switches burning in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top