I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt shower switches is that the stranded wires haven't been twisted and just put in straight.I always twist the standed cables to make one solid conductor before inserting into the terminal.My thoughts are that the screw only clamps a few strands when they are straight,leaving the other stands either side of the screw.With the load on a shower I feel this is a weak point and hence why they burn out.Obviously it can also be caused by loose terminals but back in the day when shower switches had two screws per terminal,I don't recall having to replace that many switches.Prehaps they should bring back the two screw method?
 
That's a question I'd love to see answered with something better than speculation.
The ‘theory’ that I’ve always heard touted around on this is that (think Fleming’s rules…) the direction of current in the neutral encourages the screws to loosen. My gut has always told me to claim BS on that whilst my head has always told me to find more facts either way…
 
The ‘theory’ that I’ve always heard touted around on this is that (think Fleming’s rules…) the direction of current in the neutral encourages the screws to loosen. My gut has always told me to claim BS on that whilst my head has always told me to find more facts either way…
I think that the fact that the direction of current flow in the neutral is identical to that of the live, just 1/100th of a second later, rather disproves this theory.
 
As @nicebutdim states when terminating cables into terminals they will relaxe after a minute so you need to revisit and nip them up a few times.
Oh definitely, the amount of tails that I come across in consumer units barely nipped up is staggering, I always tighten them, wait a minute, give them a bit of a wiggle any you usually find you get another complete turn of the screw fairly easily.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Blackpool,Lancashire.
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Shower switches burning
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
Bob Geldoff1234,
Last reply from
oscar21,
Replies
27
Views
2,697

Advert

Back
Top