Hi, I have a recently installed a 9.5kw shower on a 50a mcb wired in 10mm twin and earth...cable run is 2metres to a 45a switch then from that ...2metres to a dual rcd fuseboard 100a main switch with 63amp rcd x 2 ... The shower works ok on low settings but as soon as you turn it up to Eco or high it trips both the RCD's. However if you turn just one RCD on ...it will run fine on any setting low Eco or high and won't trip. As soon as you put both RCDs on and it's on Eco or high setting it trips both out. It doesn't matter wether it's on hot or cold setting either still get the same outcome as above. It's a brand new shower also. I have checked for cable damage all cables seem fine and also checked there are no crossed cables or that the neutrals are crossed on the board and are under the correct RCD bar. I'm baffled now as to why? Any help much appreciated. Thank you.
 
Hi,

Thanks for the reply,

as far as I know the results from another electrician were

live to live +200Mohms
live to earth +200Mohms


They couldn't find anything wrong with insulation resistance...

There will be a fault to earth on the neutral,try testing for that. When a high current is drawn some of that current can divert down a fault to earth,causing an imbalance which will trip RCD(s). You'll need to test the entire installation as the fault may well be on another exisisting circuit which was not apparent untill the high current of the shower enabled the fault current to reach a level to cause tripping.
 
As Richard and wire puller have said if you have a high resistance connection N to Earth then this will cause both RCD's to trip and this fault may not necessarily be with the shower it could be on another circuit so im afraid to say its get the tester out
 
I find it can be quicker to take each circuit (excluding the shower) and fully disconnect it (L/N & E) then test shower in your case, if you have a crushed cable or even a socket screw partly into a N then the issue will disappear when you get the correct circuit (circuits if 2 crushed together).
 
No mate im still here got a tad fed up with all the threads ending up a slagging match , so thought i'd pop back and have a look at whats going on

it's calmed down now. mods have clamped down on aggressive posts.
 
Oh good , was getting a tad silly I'll have to come on more often then

and back to the original thread think Darkwood has answered the question perfectly


Hopefully the waters are way calmer now and good to see you back, don't be afraid to hit the report option at the bottom left of the post if you spot other doing it again although we are keeping a tight watch ourselves, we prefer that abusive members had a break rather than the positive input of members like yourself. :)
 
Last edited by a moderator:
Hopefully the waters are way calmer now and good to see you back, don't be afraid to hit the report option at the bottom left of the post if you spot other doing it again although we are keeping a tight watch ourselves, we prefer that abusive members had a break rather than the positive input of members like yourself. :)

It's definitely better on here now. Daz
 

Reply to Shower Tripping Out help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top