Hi was called to look at a shower today which works perfectly but as you turn it off it trips the rcd in the C/U. I did an I/R test and loop test on the circuit and a ramp test on the rcd and the results where satisfactory so I informed the customer that the shower is faulty. Has anyone else had this problem? seems strange that the shower works fine though?
 
Leave shower runing - problem solved - next

Sounds like fault within shower unit and as ir and rcd tests show clear then not much more you can do except check internal connections for any obvious signs
 
Shower switch worn ???? might be disconnecting the neutral but leaving the live connected for a split second when switching off???? would that create an inbalance on the RCD?? just like some microwave ovens, if the door is slammed they operate the short microswitch and blow their internal fuse as it's opening one switch before closing the other.
 
Last edited by a moderator:
Shower switch worn ???? might be disconnecting the neutral but leaving the live connected for a split second when switching off???? would that create an inbalance on the RCD?? just like some microwave ovens, if the door is slammed they operate the short microswitch and blow their internal fuse as it's opening one switch before closing the other.

thanks for the reply. Would this create an in balance in the RCD though as once the neutral was disconnected the circuit would be incomplete and it would not matter in if live was never disconnected (for the purpose of this) the RCD should not trip? also it trips if you use the pull cord or the shower itself.
 
The only other thing I can think is if it's got some form of mains filter/capacitor/suppression ??? didn't think showers did have as such but i've know faulty filters to to blow a plug top fuse on switching off on appliances. They can power up and run fine but blow when turned off.
 
thanks for the reply. Would this create an in balance in the RCD though as once the neutral was disconnected the circuit would be incomplete and it would not matter in if live was never disconnected (for the purpose of this) the RCD should not trip? also it trips if you use the pull cord or the shower itself.

In an idea world your analysis might be valid. However in the real world, the situation is more complicated, due to the residual capacitances and leakage paths.
N-E residual capacitance exists in all installations, but the leakage through this capacitance is negligible because of the low potential (almost zero) between N-E. When the N pole of a double pole switch opens, the voltage across this capacitance will rise suddenly with a subsequent increase in N-E leakage current through this capacitance. This increase will be at a maximum if the switch N pole opens before the L pole. As the switch contacts open they will arc, causing HF voltage spikes, raising the N-E leakage even higher. If the switch has a slow break characteristic, often found in domestic switch gear, the effect will be even greater.
This phenomenon is most commonly witnessed in distribution boards with a separate front end RCD. Where opening the DB Main Switch causes a high voltage (near full mains potential) to charge the N-E capacitance of the whole installation, easily causing enough leakage current to flow to trip the RCD.
 
Last edited by a moderator:

Reply to Shower Trips RCD when turning off??? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
370
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
335
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
372

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
473
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
321

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top