Depends on many things: length of run : installation method etc etc. are you an electrician?
 
Re: Shower

to be honest, if you don;t know how to calculate cable and OCPD sizes, i don't think you should be considering doing this. if you are in training, and this is hypothetical, then say so, and assistance will be forthcoming.
 
Re: Shower

You have already asked this question here.
Ib < In < Iz

Ib you have calculated as 9500/230= 41.3A
In must therefore be equal to or greater than this and so on standard MCB values you have 45A or 50A MCB
Iz must therefore be equal to or greater than 45A or 50A depending on the device chosen.

Iz, the current carrying capacity of the cable, is dependent on the installation method and reference should be made to the on site guide appendix F or BS7671 Appendix 4 for detailed information.
Compliance must also be determined with the expected Zs and voltage drop of the circuit.
This table provides the CCC for twin and earth cables with varied installation methods.
[ElectriciansForums.net] Shower wire
 
well, it is. God made us an island for a reason. napoleon came up with the idea of a channel tunnel, thatcher's worst mistake was allowing it to be built.
 
my van does nominally 32mpg. in actual fact, it does 38mpg. so do i base the cost of a journey based on 32? nope.
 
Why 240v when the nominal voltage is 230v?

Because the manufacturer's rating of 9500W will be based on 240V. There will usually also be a lower rating for 230V, off the top of my head about 8700W. This is based on the fixed resistance of the heating element, but both these values are usually a bit on the cautious side.
 
Because the manufacturer's rating of 9500W will be based on 240V. There will usually also be a lower rating for 230V, off the top of my head about 8700W. This is based on the fixed resistance of the heating element, but both these values are usually a bit on the cautious side.

I know some manufacturers give 2 values Andy, but when they give 1 then surly you must use the nominal voltage 230 for your calculations.

What voltage would you use in an exam? I would guess that the the OP is a trainee.
 

Reply to Shower wire in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

As long as the heat input is greater than the heat losses from the container and the resistance is sufficient to limit the current to no more than...
Replies
2
Views
209
davesparks
D
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top