Final circuits, exceeding 32A don't require additional protection even though it's in a special location. As long as it's bonded. I personally thought this was a boy gash too. It's just an area the lecturer picked up on when I did my 2391.

But I do always fit an RCD.
 
It doesn't 'have' to have a RCD if it's over 32A, which it will be if it's a 9.5kW
Sorry, but that is completely wrong.
I think you are getting confused with fixed resistive loads not needing overload protection. Even with no overload protection, they do need fault protection.
And, being as the shower is in a special location, that means it must be RCD protected (if a new install).
Where does the 32amps come into it?
Distribution circuits over 32 amps, or maybe something else?
Please give us some Reg numbers to back up your strange interpretation.
 
Not notifiable.

And to be honest no one in authority cares anyway.

If there was a shower in a portakabin in a truck depot to change, thats definately not notifiable & they still don 't care.


It's all a bit silly really
 
Final circuits, exceeding 32A don't require additional protection even though it's in a special location. As long as it's bonded. I personally thought this was a boy gash too. It's just an area the lecturer picked up on when I did my 2391.

But I do always fit an RCD.

Regulation 701.411.3.3

Additional protection shall be provided for all low voltage circuits of the location, by use of one or more RCD's...
 
Setting aside best practise, manu's instructions and good common sense was the existing shower and final circuit installed under the 15th/16th Regs ? someone remind me what the regs said then about RCD protection ?
 

Reply to shower in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
277
On the minor works in the brown book it has Zdb
Replies
3
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top