mickles
-
hi everyone, an aquaintence with very little money has bought a 9.8 kw shower to replace his failed unit and asked me to fit it. house has a 6mm t/e shower cable. normally i would insist on 10mm cable, however, 9.8 kw at 230 volts works out at 42 amps. actual voltage measures at 245 which means real load is 40 amp. cable is 16metres clipped direct and is clear of insulation in the loft giving a volt drop of 4 volts ish. max tabled current capacity for cable is 46 amps and even at a current draw of 42 amps, it is unlikely the c/b would lift. in other words, it is right on the margin.
change it to 10mm or leave it? what do you think. (if he had lots of money
change it to 10mm or leave it? what do you think. (if he had lots of money