silly question? R1+R2 | on ElectriciansForums

Discuss silly question? R1+R2 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Joined
Apr 6, 2009
Messages
54
Reaction score
0
i have an assignment in which i have to describe the sequence of tests. also have to describe how the tests are done and expected values.for insulation restistence i know its 1 M ohm minimum. but is there a maximum R1+R2 value
[ElectriciansForums.net] silly question? R1+R2
 
It would depend on the type of over-current protection and circuit details, before you can determine the limit that R1/R2 should be.
There are tables which tell you the maximum Zs for a type of mcb/cable etc but dont forget that this is the external and internal impedance of the circuit and not the Ze + R1R2.
We use Amtech so we have the charts that they provide and it is self checking as you produce a certificate. But you should be able to download a chart from any decent mcb manufacturer and even some cable manufacturers.
 
Upvote 0
Hi.

1 Mohm is the minimum for a 500V test. Dont forget there are 250V and 1000V tests too.

Technically there is no max for R1+R2 but, too high a reading could lead to the loop impedance being to high to achieve the disconnection time of the relevant protective device.
 
Upvote 0

Reply to silly question? R1+R2 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top