Hi guys and girls. Got a problem on a lighting circuit.

The circuit has a junction box which I have just labeled up.
Theres only 5 lights
OUTSIDE LIGHT x2
SIDE LIGHTS x4
MAIN LIGHT
BEDROOM LIGHT x2

the main light and side lights work the problem is the rest on the light none of them switch.
A volt test shows 240v at the switches with them in both positions.

IR test shows >500 on my fluke
continuity shows fine
earthing is ok.

Anything you you need extra please ask. I'm stumped on this one. I know it's going to be something simple.
 
Easiest way is strip the JB of all cables identify each one again and reconnect the mains into the joint first then each light one at a time testing if they work as you connect - (safety in mind of course - I don't mean working live here, isolate safely between each connection made and tested).. this way you can work out where it went wrong.

You probably lost a N somewhere but cannot say for sure.
 
Hi mate firstly if you haven't already, get access to the trainee section, can you draw a diagram of what you think the connections are, you say you only have 5 lights yet your description count is 9 or am I reading it wrong?
Do the diagram and come back on, we may be able to help better with a rough idea of what you have to work with.
 
Hi mate firstly if you haven't already, get access to the trainee section, can you draw a diagram of what you think the connections are, you say you only have 5 lights yet your description count is 9 or am I reading it wrong?
Do the diagram and come back on, we may be able to help better with a rough idea of what you have to work with.

Hi should have been clearer. There are 2 outside lights wired together. 4 side lights wired together. 2 bedroom lights wired together. 1 shower room light and one main light.

The main aim light and side lights are on 2 way.

A diagram of the junction box?
 
Hi should have been clearer. There are 2 outside lights wired together. 4 side lights wired together. 2 bedroom lights wired together. 1 shower room light and one main light.

The main aim light and side lights are on 2 way.

A diagram of the junction box?

That would be good, and a pointer to which cables go where.
 
That would be good, and a pointer to which cables go where.
[ElectriciansForums.net] Simple electrical circuit
 

Reply to Simple electrical circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
726
davesparks
D
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top