P

Piratepete

A farmer client has a supply cable going underground from the DNO's kennel to a large barn converted to stables with power and light. The cable is fed from a 30 Amp switch fuse and a preceeding 30 mA RCD.

In the barn, I noted that though the power and light were on separate 2.5mm and 1.5 mm circuits these were connected together to the incoming cable by a large choc block wrapped in insulating tape! There's a separate 6mm earth wire also into said block (TT supply).

So on replacing this little mess with a 2 way garage unit I discover that the supply cable is not a 2 core SWA that it looked like, but is single core aluminium with a stranded copper insulated outer sheaf which is being used as the neutral conductor.

Does anyone recognise this type of cable and know it's normal use please?
How do I work out it's current rating?
Can I leave it? Ever tried getting a farmer to spend money on something that's been working fine for years!

Further info. It's stamped Crompton 600volt. IR to earth is 930Meg for inner core but only 3Meg for the outer neutral (NO surprise!).

Pete
 
My whole point was you said it was not suitable for burial Dave, simple as that. And in the case of a TNS supply the cable would be split concentric so only a part of the outer cable circumference would be earthed below the outer sheath.

Only in the same way as you have just said 'not suitable for burial' if I was to quote you without using your full sentence.
The sentence, which you only highlighted a part of, stated that it is not suitable for burial in a consumer's installation. You have deliberately misquoted me

Split concentric is not under discussion here, but even if it was then it would also not be suitable for direct burial in a consumers installation as the earth only covers approximately a quarter of the circumference of the cable.
 
Last edited by a moderator:
Only in the same way as you have just said 'not suitable for burial' if I was to quote you without using your full sentence.
The sentence, which you only highlighted a part of, stated that it is not suitable for burial in a consumer's installation.

Split concentric is not under discussion here, but even if it was then it would also not be suitable for direct burial in a consumers installation as the earth only covers approximately a quarter of the circumference of the cable.

We're still going round in circles, my point was that distribution rules are very different to the consumers side of things.
 
We're still going round in circles, my point was that distribution rules are very different to the consumers side of things.

Yes, and needlessly,

I clearly made the distinction that I was commenting on consumer's installations, as that is at we are concerned with on this forum and specifically in this thread.
You have then deliberately misquoted me and derailed the thread in what appears to be an attempt to make a point which did not need making in the first place.
 
Jesus, is this the 5 minute argument or the 10 minute one? Dave OCD is making the point that the DNO see fit to bury concentric cable directly, right up to and on to the customers premises. We all know what he means. Daz
 
A farmer client has a supply cable going underground from the DNO's kennel to a large barn converted to stables with power and light. The cable is fed from a 30 Amp switch fuse and a preceeding 30 mA RCD.

In the barn, I noted that though the power and light were on separate 2.5mm and 1.5 mm circuits these were connected together to the incoming cable by a large choc block wrapped in insulating tape! There's a separate 6mm earth wire also into said block (TT supply).

So on replacing this little mess with a 2 way garage unit I discover that the supply cable is not a 2 core SWA that it looked like, but is single core aluminium with a stranded copper insulated outer sheaf which is being used as the neutral conductor.

Does anyone recognise this type of cable and know it's normal use please?
How do I work out it's current rating?
Can I leave it? Ever tried getting a farmer to spend money on something that's been working fine for years!

Further info. It's stamped Crompton 600volt. IR to earth is 930Meg for inner core but only 3Meg for the outer neutral (NO surprise!).

Pete

Forget all the hair splitting nonsense being spouted, all you've done is install overcurrent/fault protection to the final circuits supplied by this cable. You have not altered the distribution circuit in any way. Note on your EIC that the distribution circuit does not comply with bs7671 and you recommend it is replaced. However it may be considered safe for continued use as long as a test and inspection is carried out yearly. --- covered.
 
Yes, and needlessly,

I clearly made the distinction that I was commenting on consumer's installations, as that is at we are concerned with on this forum and specifically in this thread.
You have then deliberately misquoted me and derailed the thread in what appears to be an attempt to make a point which did not need making in the first place.

Last post on this matter- I did not deliberately misquote you Dave, I misread and possibly misunderstood what you were getting at a little. Although you are obviously very committed to the trade please also bear in mind that I was completing my apprenticeship around the time that you were being born so I feel that I also know a bit about being a decent sparks.
 

Reply to Single Core 230Volt Supply?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top