Could the better and wiser assist with an odd one...?

I've just finished a big CU swap on a 1950's house that uses single core & earth lighting circuits. All but one of these are fine, but the faulty one is pretty funky;

There are 3 accessories on this circuit in 3 separate rooms. The first room/switch/pendant works fine. The later 2 have the same issue - with no lamp in the fittings all is well, but put a lamp into either with the switch on and 3 things happen:
- The bulb glows very briefly (30mS?)
- The RCD covering this half of the CU trips
- The 6amp type B MCB covering the circuit trips

If this was just an RCD issue I'd be confident of a neutral/borrowed neutral issue, but how can a bulb (which doesn't blow/fail during this) cause an MCB to trip?

It's got me going round in circles so any clarity and advice is most welcome.

Thanks
 
There is a minor disadvantage in wiring in singles not in conduit which is that where the 'go' and 'return' are not in the same cable, i.e. the currents are not balanced, noisy LED drivers (and before them, noisy CFLs) emit more radio interference. Also happened with traditional fluorescents but those were less common in a domestic install.

No sign of MCB tripping during this round of tests so I'm putting this down to a poor MCB,

Sorry, doesn't make sense. The MCB only knows how much current is going into the load, not where it goes afterwards. I'm not saying you haven't fixed the problem, but as yet there's no explanation of why the MCB was tripping, be it rich, poor or completely skint. I don't like unexplained phenomena.
 
Yes Charlie, live looped through switches (2-way in the second room) and neutrals/earths looped via pendants - bonkers system IMHO

It's the most logical system and replicates the way lighting is wired in conduit.
I say it's the most logical because you take each conductor to where it is needed rather than taking it to places it is not needed and then jointing it.
 
It is, however, harder to alter, in a way that does not mirror conduit work. E.g. adding a point to a normal looped conduit system, you are almost guaranteed a route through the existing conduit to get the two sides of the circuit together ready to head off to the new point. But with singles run separately in a domestic situation, you may well have to access two locations; getting the neutral from the rose might be easy, but then you have to open up elsewhere to get at the line, and if you can't add a cable down to the switch, you are forced to add a junction box, possibly in an undesirable position. Neither of these are necessary if the line is looped at the rose too.
 

Reply to Single core and earth lighting fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top