EWebster

Hi all,

A customer doesn't want a new consumer unit, but wants work doing to an existing lighting and existing ring circuit.

I believe I'm correct in thinking that if I do work on these older circuits, I must then RCD protect them. Is it better to fit an RCD to the incoming mains, before the fuse box, or individually RCD protect each of the two circuits?

Many thanks

EW
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.

Sounds like a plan. I'm assuming I can get push in RCBOs to replace the fuses?

Regards
 
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.

Why do you say that he needs to fit a main switch before the rcd ?
 
As an rcd should not be the main mean of isolation for the installation.

I spoke to NICEIC yesterday, and he cited the regs, saying that there is provision in the regs for using an RCD as a main switch.

Seems to be a bit of confusion around this area. :confused:
 

Reply to Single main RCD or multiple in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top