Amp David

-
Mentor
Arms
Joined
Oct 2, 2009
Messages
5,114
Reaction score
904
Location
Glossop
Installed a garage CU, 2 way. As the house is TNC-S an earth rod has been installed, which is giving an Ra of 102 ohms.

The supply to the garage is protected by a MCB on the non RCD side of the CU, as installation methods don't require RCD protection.

The circuit in the garage has been protected by a 30ma type B RCBO. It is only single pole. I have today been told that it has to be of the double pole kind. Have I messed up?:confused:
 
As you have derived a TT form a TN-C-S then there is a possibilty of a PD arising between the combined neutral & earth of the PME and the true earth of the TT system under earth fault conditions should the RCBO operate and disconnect only the live.

Unless you are there to switch the main DP isolator off at ther same time, thiscan't be relied upon.
 

Reply to Single or double pole RCBOs??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
518
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
459

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
794
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K