:cry_smile: My facial expression with this job I can't figure out.
Hello first post on here and been searching to see if they was a post like this online.
In a church building, there is a 3 phase board that feeds a wylex single phase ccu with a swa cable 3 core but not sure on size, my best bet is it looks like a 25mm. This single phase board is protected by a mcb 50A within the 3 phase board. Now the single phase board is a spilt load ccu. The main breaker for the single phase ccu is 100A, with two rcd rated at 80ma standard on most ccu. looks like a twelve way board. Now here is the problem. From that single phase board are two radial circuits 32A 4MM s.w.a 4 core, and everytime we plug in 3 pin heaters on the two circuits within 30mins or sometimes 1 hour (varies) it trips out the 50a mcb at the 3 phase board, which means it bypasses the 32a mcb on the single phase,main switch and rcd altogether. Whatsup with that.
At first I thought it was overload but did the formula to find that a 32A circuit can take about 7200 watts, 3 heaters on one circuit each about 2kw.So that ruled out overload, I don't think its a short because of the duration the circuit stays on for before it trips. I was hoping it was the way that they used one s.w.a 4 core to wire 2 radial circuits(shared neutral) basically instead of using a 5 core or running two sepaerate cables back to the board its just the one.But still trips 50A breaker.
I don't really know anything else about the circuit like supply type, but could find out if you have any ideas. Discrimination comes to mind about way it doesn't trip the closet mcb(lowest)i.e 32 a breaker. But other than that I just don't know. Please if you have time remember to reply, we need the heating for the homeless, I am a Electrician struggling, asking my brothers and sisters in arms to shed some light. Thanks
Hello first post on here and been searching to see if they was a post like this online.
In a church building, there is a 3 phase board that feeds a wylex single phase ccu with a swa cable 3 core but not sure on size, my best bet is it looks like a 25mm. This single phase board is protected by a mcb 50A within the 3 phase board. Now the single phase board is a spilt load ccu. The main breaker for the single phase ccu is 100A, with two rcd rated at 80ma standard on most ccu. looks like a twelve way board. Now here is the problem. From that single phase board are two radial circuits 32A 4MM s.w.a 4 core, and everytime we plug in 3 pin heaters on the two circuits within 30mins or sometimes 1 hour (varies) it trips out the 50a mcb at the 3 phase board, which means it bypasses the 32a mcb on the single phase,main switch and rcd altogether. Whatsup with that.
At first I thought it was overload but did the formula to find that a 32A circuit can take about 7200 watts, 3 heaters on one circuit each about 2kw.So that ruled out overload, I don't think its a short because of the duration the circuit stays on for before it trips. I was hoping it was the way that they used one s.w.a 4 core to wire 2 radial circuits(shared neutral) basically instead of using a 5 core or running two sepaerate cables back to the board its just the one.But still trips 50A breaker.
I don't really know anything else about the circuit like supply type, but could find out if you have any ideas. Discrimination comes to mind about way it doesn't trip the closet mcb(lowest)i.e 32 a breaker. But other than that I just don't know. Please if you have time remember to reply, we need the heating for the homeless, I am a Electrician struggling, asking my brothers and sisters in arms to shed some light. Thanks