Hi everyone,

I have moved into a property with a 63a single pole rotary isolator controling a inline water heater. Is this safe? Surely it should be a 63a two pole isolator switching both the live and neutral?

Any advice would be much appreciated.

Thanks.
 
a high current appliance should isolate both live and neutral

The current is unimportant, as you can get just as bad a shock from a 6A circuit as a 60A. On a domestic single-phase circuit, an isolator (which you would turn off to enable maintenance, for example) is expected to break all conductors with a 3mm contact separation. A control switch need only break the line, so is it possible that this was the intended purpose of your rotary switch, and the means of isolation (if required) is something else?
 
The current is unimportant, as you can get just as bad a shock from a 6A circuit as a 60A. On a domestic single-phase circuit, an isolator (which you would turn off to enable maintenance, for example) is expected to break all conductors with a 3mm contact separation. A control switch need only break the line, so is it possible that this was the intended purpose of your rotary switch, and the means of isolation (if required) is something else?
Thanks for your reply, I would imagine the rotary switch would be used for maintenance as the only other way to isolate the water heater would be from the 50a MCB at the board. Perhaps I am wrong and it is just used as a control switch.

So for use as an isolator for maintenance it would need to break live, neutral and earth?
 
Thanks for your reply, I would imagine the rotary switch would be used for maintenance as the only other way to isolate the water heater would be from the 50a MCB at the board. Perhaps I am wrong and it is just used as a control switch.

So for use as an isolator for maintenance it would need to break live, neutral and earth?
Never break the cpc!!!!!
 
I'd be surprised if it is a Single pole rotary isolator, more likely a Double pole but only one pole used so shouldn't be too hard to rectify.
Any pictures of the internals?

[ElectriciansForums.net] Single pole rotary isolator
[ElectriciansForums.net] Single pole rotary isolator


[ElectriciansForums.net] Single pole rotary isolator
 
Last edited:

Reply to Single pole rotary isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
662
For a TN system neutral is deemed at earth potential.
Replies
6
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top