Hi All,

I'm after a little help/advise from anyone who has any knownledge or experience in a single to 3-phase inverters.

My scenario:
We're in the final process of finishing a care home rewire, they have a 3-phase lift being installed. Everything's in place and been ran etc...

UK power networks has just given the owner a quote of over 100k to upgrade the current supply to a 3-phase supply to accommodate the 3-phase lift.

Has anyone ever fitted a 3-phase inverter? The installation currently has a 100amp supply but the loading is minimal. The lift is 31.7amps (37.8amps start up). Can I supply a 3-phase inverter with a 6mm 40amp MCB from my single phase and then supply the lift that way.

Has anyone ever installed one before? Recommendations or advise is much appreciated.
 
The biggest 1-3 phase inverters I use top out at 2.2kW, you're talking ten times that size. Plus, supplying 40A of 3-ph startup off a single line is going to fully use that 100A supply, then some more.

Bottom line, if your client wants a 20kW lift motor, they need to stump up for 3 phase incomers.
 
A standard motor inverter would not work anyway due to the fact you are not just feeding a motor, you would be feeding controls, lighting, etc.
Only option would be a rotary converter for this type of application, but even then I do not think the supply you have available is big enough. May be worth investigating though, as UKPN may be able to increase the size of the existing single phase supply for a lot less than ÂŁ100k
https://www.simplypowersupply.com/pdf/mtrt.pdf
 
Didn't he say 40A was the start-up current ?
Which is more like 10KW
Where did 22kw come from ?

22kW was off my head with no working. Looked it up and an 18kW 415V motor at 0.8pf pulls ~32A FLC, as stated in the OP. To power that same 18kW off a single phase supply is 97A before conversion losses! I don't know where he got 37.8A startup from, a heavy traction lift motor is more likely to pull 100+ at startup.
 
Good planning on the designers/builders/lift owners parts of going ahead without checking the feasibility of 3 phase first...

What is the expected usage of the lift? i.e. frequency of use, weight in it etc?
 
Who thought it would be a good idea to design a 3 phase lift into a single phase house? Do they not do single phase lifts?
 
The lift is only small, and is literally going from ground to first. I've worked in one of their care homes before and the lift which was installed there was literally supplied via a 13amp plug top.

Apparently this specific lift will only come as 3-phase.
All the carriage lights and shaft lighting is supplied separately by a seperate DB situated in the corridor cupboard. Looking at the Lift document it says total running current 26.5 amps and total starting current 37.1 amps.

I was under the impression this was across phases so running current roughly 9 amps per phase, and starting current 13amps per phase.
 
I've just attached a screen shot of some specs on the drawings

[ElectriciansForums.net] Single to 3 phase converter
 
Somebody better speak to the Lift installation company before any more plans are made I doubt they will accept an inverter supply.

The lift will form part of the Fire Escape route, it will have to be bullet proof.
Will it? Every block of flats I've ever done the lift is grounded in the event of a fire.
 
Will it? Every block of flats I've ever done the lift is grounded in the event of a fire.

It's not a block of flats with able bodied people in it.

A true Fire escape lift is isolated from the main building and the power supply is run in a route so as not to be affected by Fire.

Even if the O.P lift is not a true Fire escape lift, it may well form part of the Fire escape strategy if Care home residents are above ground floor level.
 

Reply to Single to 3 phase converter in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top