Hi All,

I'm after a little help/advise from anyone who has any knownledge or experience in a single to 3-phase inverters.

My scenario:
We're in the final process of finishing a care home rewire, they have a 3-phase lift being installed. Everything's in place and been ran etc...

UK power networks has just given the owner a quote of over 100k to upgrade the current supply to a 3-phase supply to accommodate the 3-phase lift.

Has anyone ever fitted a 3-phase inverter? The installation currently has a 100amp supply but the loading is minimal. The lift is 31.7amps (37.8amps start up). Can I supply a 3-phase inverter with a 6mm 40amp MCB from my single phase and then supply the lift that way.

Has anyone ever installed one before? Recommendations or advise is much appreciated.
 
It is correct that a lift for general use could be incorporated into an escape plan in an emergency situation after a risk assessment and a controlled strategic plan but generally this would be considered a high risk policy. Lifts which have been put in place as part of an escape route are subject to strict legal requirements and are generally only considered where vertical footfall is not free flowing such as a hospital where mobility may be restricted.
 
The motor is rated at under 12kW.
You can use a 1ph - 3ph VFD to control just a 3ph motor. The existing controls would be wired to the VFD controls, fairly simple if you understand the way the lift works and safety requirements etc.
But will the lift company want/know how to redesign their lift for a one off project?
No.
 

Reply to Single to 3 phase converter in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top