We have to install 3 x 240mm singles and 1 neutral to a panel in a LV room.the ducts aren't large enought.What happens if the singles are split through 2 ducts.IE, 2phases in 1 duct and the other phase and neutral in another duct.Where might i find a contradictory regulation.
 
This would appear to go against regulation 521.8.1

However, if you could fit 4*120mm in one duct, and 4*120mm in another so you have a parallel arrangement but each duct has all live conductors of that parallel set, it would appear to be OK.
Absolutely this. But only if the ducts are the same length!
 
Yes, a good point!

Still, as long as the length of cable in either route is sensibly similar than it ought to be fine. Not sure what that actually translates in to but I would guess 5-10% max difference might be reasonable (so long as a similar level of current imbalance is not pushing one set above its CCC rating)?
 
Whilst I agree its non-compliant as far as regs go but, does the line within the NICEIC test certifcate EIC) which ends -
"2018+A2:2022 except for the departures, if any (Regulations 120.3, 133.1.3 and 133.5), detailed as follows:"

provide some sort of caveat for non-compliant but equally safe work?

May not necessarily apply in this instance?

Opinions?
 
This would appear to go against regulation 521.8.1

However, if you could fit 4*120mm in one duct, and 4*120mm in another so you have a parallel arrangement but each duct has all live conductors of that parallel set, it would appear to be OK.
Wouldn't necessarily need to be 120.0 a basic calculation gives 95.0 which may in parallel fit the duct. Other factors would need to be calculated however.
 
Whilst I agree its non-compliant as far as regs go but, does the line within the NICEIC test certifcate EIC) which ends -
"2018+A2:2022 except for the departures, if any (Regulations 120.3, 133.1.3 and 133.5), detailed as follows:"

provide some sort of caveat for non-compliant but equally safe work?
To some degree it would depend very much on the nature of the ducting and routes they take. My concern with this is you could get a significant magnetic field between the two runs due to the lack of current balance (cancellation) on each pair of conductors and so if they are separated by far, or ducts form some sort of a magnetic path, it might cause trouble.
 
Wouldn't necessarily need to be 120.0 a basic calculation gives 95.0 which may in parallel fit the duct. Other factors would need to be calculated however.
True, cooling is generally better with parallel split. I just halved the OP's value as should be more or less the same VD, etc, and at least as good CCC.
 
The rules on parallel conductors are very clear: same length, same OCPD, same terminations. That’s why there’s no other derate factors applicable - doesn’t matter how many cables there are (we always assume two sets but no reason for three or more), it’s the same circuit.
 

Reply to Singles in ducts in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
403
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
991
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think a 3 legged breakout boot would be your best bet in the circumstances.
Replies
3
Views
619
davesparks
D
  • Question
Double pole switches? Mounted on a grid module? Ignore the fact they have a N stamped on them. Or is your 2 gang switch decorative, and you...
Replies
3
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top